      Hello everyone,im happy some issues with the ac on my 95 integra ls..
      during the night it performs okay,but during the day i am not happy with the ac temp during sunlight hours,i live in miami and its veeeery hot n humid right now..
      i did the ac performance check and got interesting results,with the recycle button off i only dropped from 87 degrees to about 70-69 degrees…i performed a pressure test and only got interesting results after running for about 5 minutes the the ac on my low side seemed a little low,less then 30 psi,while the high side seemed a little high,at about 200 psi….i thought it could be a possible blocked expansion valve but when i accelerate the engine the low side drops quickly and comes back up when i let go of the gas…so im a bit baffled any feedback will be appreciated,im going to attach two pictures,the pressures with the ac off and on thanks in advanced

      Attachments:
    Viewing 13 replies - 1 through 13 (of 13 total)
    • Author
      Replies
    • #465694
      Jason Alexmckrishes
      Participant

        that seems low, unless the temperature outside was in low. I would recommend watching all of Eric’s vidoes on HVAC:

        http://ericthecarguy.com/videos/7-videos/25-hvac

        Very informative and can help you on your way to an informed diagnoses.

        #465715
        college mancollege man
        Moderator

          I would suggest that your system is low on charge.

          #465724
          osmilosmil
          Participant

            I should also add for the first couple minutes the pressures were about 40 on the low side and about 250 on the high side, not sure why it would go down after a couple minutes of running

            #465728
            college mancollege man
            Moderator

              The pressures start higher due to the system start up and air temp load
              being high.after a few minutes the air load decreases and pressures come
              down.I see that you have a set of manifold gauges.do you have R134a and a
              scale?

              #465731
              osmilosmil
              Participant

                Thanks for that information and yes i do have r134 freon and a digital scale

                #465732
                John B KobberstadJohn B Kobberstad
                Participant

                  [quote=”ozz420″ post=32106]Hello everyone,im happy some issues with the ac on my 95 integra ls..
                  during the night it performs okay,but during the day i am not happy with the ac temp during sunlight hours,i live in miami and its veeeery hot n humid right now..
                  i did the ac performance check and got interesting results,with the recycle button off i only dropped from 87 degrees to about 70-69 degrees…i performed a pressure test and only got interesting results after running for about 5 minutes the the ac on my low side seemed a little low,less then 30 psi,while the high side seemed a little high,at about 200 psi….i thought it could be a possible blocked expansion valve but when i accelerate the engine the low side drops quickly and comes back up when i let go of the gas…so im a bit baffled any feedback will be appreciated,im going to attach two pictures,the pressures with the ac off and on thanks in advanced[/quote]

                  Low Side PSI____High Side PSI____Temperature

                  25-35______________135-155___________65F
                  35-40______________145-160___________70F
                  35-45______________150-170___________75F
                  40-50______________175-210___________80F
                  45-55______________225-250___________85F
                  45-55______________250-270___________90F
                  50-55______________275-300___________95F
                  50-55______________315-325__________100F
                  50-55______________340-345__________105F

                  ——————————————————-

                  L_____________________L__________System low charge

                  L_____________________H__________Blocked expansion valve

                  H_____________________L__________Reed valve in compressor
                  (Needles vibrating)_________________bad

                  H_____________________H__________System overcharged

                  #465744
                  college mancollege man
                  Moderator

                    [quote=”ozz420″ post=32147]Thanks for that information and yes i do have r134 freon and a digital scale[/quote]

                    since you have a scale and refrigerant. you could recover the system
                    charge.evacuate the system and weigh the entire charge in and be done.
                    option 2 would be to hook up the gauges. weigh in 4-6oz see if the cooling
                    gets better.if it does your on the right track.I don’t think your charge is
                    that far off.

                    #465841
                    osmilosmil
                    Participant

                      Thinking about adding a bit of uv dye to check for small leaks,also what do you think about red angel ive been hearing it works very well

                      #465917
                      osmilosmil
                      Participant

                        Thinking about adding a bit of uv dye to check for small leaks,also what do you think about red angel ive been hearing it works very well

                        #465924
                        college mancollege man
                        Moderator

                          use a dye that can be seen with a black light.

                          #466016
                          college mancollege man
                          Moderator

                            use a dye that can be seen with a black light.

                            #466067
                            EricTheCarGuy 1EricTheCarGuy
                            Keymaster

                              Honestly those pressures look normal, the low side could be a little lower and the high side a little higher if I’m honest. You might have a slightly low charge. Check the cooling fan operation, they BOTH need to come on with the AC. Since you’re running 134 in an R12 system it won’t cool as well and leaks around the fittings are common. You might try injecting a little dye and adding a small charge to the system to see if cooling improves.

                              #466161
                              EricTheCarGuy 1EricTheCarGuy
                              Keymaster

                                Honestly those pressures look normal, the low side could be a little lower and the high side a little higher if I’m honest. You might have a slightly low charge. Check the cooling fan operation, they BOTH need to come on with the AC. Since you’re running 134 in an R12 system it won’t cool as well and leaks around the fittings are common. You might try injecting a little dye and adding a small charge to the system to see if cooling improves.